how many amps in 1 KVA? V=440v, PF=0.8 and FREQ=50Hz
Answer Posted / deepak
KVA(Apperent Power)=1.732 * Line voltage * line Current(It
is in Three Phase System)
According to above formula
I= KVA/1.732*Line Voltage
I=1000/1.732*440
I=1.312Amp.
Is This Answer Correct ? 7 Yes 4 No
0
Ameerlal
Re: how many amps in 1 KVA? V=440v, PF=0.8 and FREQ=50Hz
Answer
# 13
kva=1.732*v*i*cos
i=kva/1.732x440x0.8
i=1.6A
| Is This Answer Correct ? | 1 Yes | 0 No |
Post New Answer View All Answers
Why power factor should not be in leading (capacitive) mode of any load.
why dc is used in control circuit for mv & hv switchgear instead of ac
As you achieve greater success with the company after some years, Will you like to be a share holder in our company?
can anybody tell me that for p.f. Improvment we use capacitor banks but how to decide its capacitance. As we all know how to calculate kvar but what abt capacitance value
What is the effect on Power factor and capacitor when your company load is more than 70 % of welding transformer
how is capacitor bank look like
what is the most permissible winding temp when we conducting a generator load test?(condition no load)
What are the types of transformers according to the arrangement of iron cores?
dg started in plc mode and load taken later one battery terminal connection will be disconnected by loose connection what will happen for dg and shall we connect battery terminals while dg in load time?
Where voltage are high and current to be interrupted is low the breaker preferred is:
How to calculate main incomer rating of APFC Panel ? Let's say i want to find main incomer for 11kV, 1000kVAR Panel.
what is lumped and distributed elements?
What is mean by STUB protection?
describe the phenomena of vacuum interruption in C.B
What is dynamo?How it works and what is the function of dynamo in a DG.