how many amps in 1 KVA? V=440v, PF=0.8 and FREQ=50Hz
Answer Posted / deepak
KVA(Apperent Power)=1.732 * Line voltage * line Current(It
is in Three Phase System)
According to above formula
I= KVA/1.732*Line Voltage
I=1000/1.732*440
I=1.312Amp.
Is This Answer Correct ? 7 Yes 4 No
0
Ameerlal
Re: how many amps in 1 KVA? V=440v, PF=0.8 and FREQ=50Hz
Answer
# 13
kva=1.732*v*i*cos
i=kva/1.732x440x0.8
i=1.6A
| Is This Answer Correct ? | 1 Yes | 0 No |
Post New Answer View All Answers
hi can anyone pls tell me the eee interview core questions asked in l&t
HOW TO DESIGN THE body EARTH cable(Copper Conductor) size for 60KVA UPS?
2. What are the parameters of EHT sub-station?
sir, what is the importance of Fault MVA. how to calculate fault mva of 33kv substation connected by 6.5 km line(single circuit with equal spacing) with 110/11kv transformer in 110kv susbstation.the fault mva on 11 kv bus in 110kv susbstation is 208mva.
why to use freewheeling diode ( diode in revers bias mode) across dc coil
Why should we hire you over the others waiting to be interview?
why a tester wont shock while testing the power in house
Why line VTG = √3 phase VTG in star? How?
1600 KVA ka transformer hi aghar lt side par 800A aur voltage 420 ho to HT side ki cable ki rating keya ho gi?
how much cable size required for 70 kilowatt load.
How will polarity test of Dy5 Transformer ?
What is value of earth resistance required for substation and equipment earthing and what are the reference guidelines
Can you any one explain application of buccholz relay operation and pressure relif device operation of power transformer
How to select the proper VSD to operate high inertial load
how to find the resistance and gap volatage of the diode??