How much current can 11KV line carry? What are the
formulae used to calculate current across both side of
transformer? Moreover I need to know can I connect 33KV
line with transformer of 1600KVA? Details are: V=415,
Pf= .9
Answer Posted / manimaranmuthu.m
11KV PRIMARY CURRENT[HT]:
KW = KVA*PF
POWER [KW]= 1600*0.9
POWER = 1440 KW
POWER [KW]=√3*KV*I*PF
root(3) = 1.732
1440 = 1.732*11*I*0.9
1440/1.732*11*0.9 = I
I = 83.98 AMPERE
415V SECONDRY CURRENT[LT]:
WATTS = 1.732*V*I*PF
1440*1000 = 1.732*415*I*0.9
I = 2226 AMPERE
| Is This Answer Correct ? | 29 Yes | 13 No |
Post New Answer View All Answers
can any one suggest me the tilt angle of my solar pannel ?? or tell me how can i know the fix tilt angle of my solar pannel?? my cordinates are 31.503629,72.993164.
what is formula for calculate thermal overload in new numiricalrelay( not in bimetal relay)?
What is the difference between the relay and the circuit breaker?
what is the difference between neutral and earth
DC transmission
what are the maximum available current, voltage ratings and switching speeds of the power electronic devices thyristor, power mosfet, igbt, and mct?
What is the difference between Generator Differential Relay and Transformer Differential Relay?
for what purpose the star point is done in ct
How you give clearance to a spare feeder.
Give details of your interested designation, the post you are interested to serve the company better and explain why you think you can serve the company better in such position if employed?
how many Classification of fire extinguisher
what is the circutor?why we use it ?
Why magnetic flux produces an induced current?? what is the detailed procedure ?? ans plz
what is effect of leading power facter on the system and billing
Give some differences between open loop and closed loop?