What will be the minimum megger value of 1700 KVA Transformer?
a) Do megger value varies according to climate conditions
and area .
b) If megger value is 100 mega ohm is it good for new
transfomer.
Explain?
Answer Posted / shariff
There is no minimum or max. value for any transformer
Insulation resistance values( not megger value),the main
factor here is the polarization index value .ie, the IR
value should decay with the time of the time of applied VG.
and the ratio of PI should be morethan 1,and the climatic
conditions will decay the IR values.
Is This Answer Correct ? | 0 Yes | 1 No |
Post New Answer View All Answers
For group 1 , 2 whather i have to prepare my technical or general studies etc? and im graduate in ee engg. for wht posts im eligible for? please tell me!
I have a CT meter with ratio 60/5. The meter reading of previous month was 3290.49 and that of current month was 3797.26. How many chargeable units as per normal meter should be my reading.
what will be the min and max voltage flow from neutral to earth?
why we use four type of phase angle difference between pimary & secondry winding of a transformer & where we use them?
Which do you think is the most significant cause of energy loss in a factory?
Is MEN and RCD related to each other ?? IF yes then how??
what is interfacing in computer studies?
how to calculate cooling requirement of datacentre from electrical load?
why do we carry out winding resistance test?
pls tell me function of closing coil of A.C.B.
why effective resistance should be more than static resistance in transmission line?
HOW TO CALCULATE THE REGULATION OF 100 AND 25 KVA TRANSFORMER
can i use 2000/5A Clamp meter to measure HT cable
What are the types of instrument transformer?
how much flux density of CRNO core