what do you mean by the "bay" in a switchyard?
how to determine exact number of bays in a substation?
Answer Posted / shibuss
The interconnection of the following equipments forms a Bay
1. Line isolator with e/s and bus isolator
2. Lightning arrestor
3. Potential transformer
4. Current transformer
5. Circuit Breaker and
6. Carrier communication equipments
The following are the type of Bays
1. Incoming feeder bay
2. Outgoing feeder bay and
3. Transformer bay
The number of bays are selected based on the number of
feeders incoming and outgoing and the number of transformers
Is This Answer Correct ? | 88 Yes | 11 No |
Post New Answer View All Answers
What happened ,If 3 phase clearance not maintained in 33KV Line,11KV LIne etc?
if we look on phasor of the transformer vaoltage is 180 oppsite at primary and the secondary so to improve a power factor is secondary should kept negative to improve it primary side means is -.90 became +.90 at other side
in control panel, how can i measuring the distance between one bus bar to another bus bar. then now only for bus bar. in mpcb and contactor also. that means one mpcb to another mpcb how much distance? how can i calculate that.
what is KA rating and how can we choose switchgears on applications
circuit diagram of trip circuit supervision relay
What is the tension required for the 25000 CFM AHU belt
what is the Connected Load (kW) or Contract Demand (kVA)of mahindra nasik plant??
What is thresh hold value of current?
Why only sinusoidal ac voltages are generated?why not triangular or sawtooth?
pls tell me function of closing coil of A.C.B.
What should be the length of transmission line so that we can see/obtain the full sine wave of voltage??
what is earthing.how we make it,describe briefly.
What kind of socket shall be provided for window type air conditioner with cooling capacity upto 18000 BTU/hr
what is the role of transistor in Circuit?
could you measure current in parallel?