how to calculate knee point voltage of current transformer?
Answer Posted / arup
Knee point voltage, Vkn = (VA X ALF)/ In
VA= Burden =30 (Say)
ALF= Accu. Limit. Factor = 20 (Say)
In= Rated Secondar Current =5 amp (Say)
Then Vkn= 120 volts
If CT Ratio is 2000:5 then In=5
Class is 5P20 then ALF=20, P=Protection CT
| Is This Answer Correct ? | 37 Yes | 10 No |
Post New Answer View All Answers
WHY EARTHING NOT NEEDED IN BATTERY IN SUBSTATION
what parameters should we check to reduce the power bill
In a large office how do we calculate required number of light fittings, assuming fittings are 4x18W or 2x36W fluorescent fitting ?
What are the advantages and disadvantages of the dc motors?
How to measure the earth resistance value in a concrete pavement(flood light area)?
Can the output voltage of a rectifier be greater than the input AC voltage without the use of any voltage multiplier in the circuit??please provide the explanation too..
Can we use a absolute encoder to show rpm of a motor ? what about the condition when power is off ? what is difference if a incremental one is used ?abanirout@gmail.com
Classify drilling machines.
please explain how to do 'pole drop test' on generator?
Haw to check conductivity of budbar
What are the components connected in between the power supply coming from an electric pole to HT & LT Panels in a large commercial building or how the power supply connected from Electric pole to Transformer & then to the HT & LT panels of a building? Please send me answers via mail, my id is yogiagarwal@gmail.com. If possible, please give a line diagram.
What are the function of different components of servo motor?
I have motor 1500 HP and , 4160 V , 60 HZ , then i need the rating of transformer which can feed that motor ??
what is the circulate the diesel in DG in side pls tell parts name and picture with circulate the diesel
What is the RME and explain the full form and what is the RME work?