Generator Protections are:
1. over current protection
2. Earth Fault protection
3. under voltage protection
4. pole slipping protection
5. under frequency protection
6. Impedence protection
7. df/dt protection
Transformer Protections are:
1. Differential protection
2. winding temperature protection
3. Oil temperature protection
4. overcurrent protection
5. Earth fault protection
6. undercurrent protection
Note:
The protection relays are increases deponds on the ratings
of the Transformer and Generator...
| Is This Answer Correct ? | 10 Yes | 2 No |
Post New Answer View All Answers
what is self capacitance of inductor
Which contains in POLE ASSEMBLY of a 11KV Kirloskar-make SF6 (Model No-FP620A12)? Will u clarify with drawing?
If you have an earth with pilecap then your resistance is really low. why and how?
Igfet is a
Give some differences between open loop and closed loop control systems.
i have applied for junior engineer 2 c&w for Guwahati RRB please send me last five year question paper
if there are six generators (3 gas CATT, one Jenbacher o1 MW each, and two nos Diesel 01 no 01 mw other 0.65mw EDGs ( say), 3 CAtt gas set have identical pole pitch,01mw EDG and Jenbacher gas Set have different pole pitch, how their power connection can be done to connect a common bus bar during installation. in short, how different pole pitched generators power connection can be done to connect a common busbar system through generators incomer ACBs.
How do you compute voltage drop and cable size over distance?
armature winding of dc machine produce alternating emf then it convert in to dc by using commutator.But only we consider armature resistance why don't we consider inductive reactane effect?
How maesure earth neutral value & how much maximum value value required in between earth & neutral.
If we have 11 kv RYB Phase single core cable near about. Then wht effect and losses
I WANT YHE TECHNICAL AND ELECTRICAL SPECIFICATIONS OF 2x4MW 11KV 2x10MW 11KV 2x25MW 11KV 2x100MW 11KV HYDEL POWER PLANT i.e PROTECTION SYSTEM,MONITORING,CONTROL SYSTEM,GENERATION,SYNCHRONISATION,METERING PLEASE SEND THE DETAILS TO MY MAIL ID SPRAVEEN_222@YAHOO.CO.IN
what is the Earth Voltages in Power Plants, Sub-stations, Industries, Residential & Commercial Buildings.
Is it advantages of having star-delta vfd than normal star vfd , if yes why?
What is meant by RVT and NDR ? expansion and details of it