What is a liquid resistance starter?where it is used??
Answer Posted / ameeya(acc)
lrs is used at the time of starting of slipring induction
motor(HT) to reduced high starting current and create high
starting torque.as the name indicates here water and costic
soda works as resistance .bcoz slip ring ind.motor rotor is
nt shorted.so this work can be done through this reistance
| Is This Answer Correct ? | 20 Yes | 7 No |
Post New Answer View All Answers
when ac current flows thru d coil of a contactr,it energizes,magnetic field attracts d contact of the coil...nw wont dt ac current in d contct induce current back on to d coil thru mutual inductance leading to high currnt in d coil
What is the use of bundle conductors?
Best way to measure the Soil resistance of rocky soil, three probe method and four probe method
what is the principle of the single phase energy meter? and,what is the advantages and disadvantages of single phase energy meter?
can i able to get bhel previous exam question paper?
what curve and rateing would you use for a three phase 0.75kw motor?
why ahould you show client/engineer activities clearly on the project plan
What is the Difference between Ac Drives and Dc Drives? According to application, speed, Torque, cost, Reliability, Construction, Motor etc... Thankyou !!!
if we look on phasor of the transformer vaoltage is 180 oppsite at primary and the secondary so to improve a power factor is secondary should kept negative to improve it primary side means is -.90 became +.90 at other side
What is the difference between amorphous core transformer and CRGO core transformer?.
What is the difference between voltages or potential difference? And what are they?
what is the circutor?why we use it ?
100 MVA 3-phase alternator with earthed neutral has a reactance of 5 ohms per phase. what will be the fault MVA of generator.
I need to connect a synchronous generator to the grid using automatic synchronization and two circuit breakers (one for synchronization, one for end connection to the grid), how to determinate the required diameter of the cables?
Different STANDARDS (BS, IS, IEC etc) gives different informations on CT specification. How they correspons w r t each other (i.e I mean to say BS provides "knee point voltage" but IS does not, then how can i select CT)