Is it necessary to place tap changer in secondary winding or
we can use on both sides?
Answer Posted / dffg
As i know it is used at the hc side of the
tranformer.Becouse there are more windings on that side and
so it is easier to make a regulation.
| Is This Answer Correct ? | 2 Yes | 1 No |
Post New Answer View All Answers
How do i carry out or know the vector group of a Dyn1 and Dyn5 transformer
In electrical what is earth(ground)connection, wht is the importance of it, why it is recomended to maitain below 3VAC between Neutral and earthspecially in PLC used machines?
To prove the capacity of a 10MVA transforemr with 6.5% impedance by a short circuit test how much power is needed to inject an impedance voltage if we have to arrive for its rated current?
How to do cable sizing calculation for 750 A Neutral Earthing resistor for 33kv. the 33kv cable going to swbd. is 630mm2 3 runs.
what is magnetizing and demagnetizing current in generator and motor?
How to calculate no of EARTH PIT? Describe the formula as per IS standard?
pre arcing time of ehv breaker
how to select the mpcbs and contactor for 3 phase 30 hp star delta motors.for plc control.and tell me the calaculation for future use.
What is the working principle of CFL & T5 tube light & 40W tube light with electronic ballast?
What is real time power factor control panel(RTPFC)?
Why is water motor not taking the pressure? what is the problem?
how to calculate the capacitor to maintain power factor?
why they were using TRIAC instead relay in some controllers and what is the advantages.
plz send me the syllabus or any sample paper for engineer trainee recruitment if any,on ravinder911@yahoo.com
what is a bus post insulator? explain its application in a substation.