Answer Posted / nilesh
since excess of leading current flows it heat up dielectric
medium between two plates and excessive current burns the
capacitor.
| Is This Answer Correct ? | 6 Yes | 0 No |
Post New Answer View All Answers
Why 15Amp. MCB is suitable to carry load of 1.5Ton Ac please Explain?
why i can not use thimble on capacitor duty contactor
what is p.s impedance measurement test in earthing transformer?
What is error of a measurement?
what is the ATS .And how it works.
WHAT IS DEGREE OF COMPOUNDING IN D.C MACHINE MEANS? HOW TO READ THE OPERATING CHART FOR ANY ELECTRICAL MACHINES?
Why is negative feedback invariably preferred in closed loop system?
What is fault clearing time for Current Limiting Moulded Case Circuit Breaker?.
Operation of isolators.
what is two point starter?
What are the special cables required for explosion proof wiring?
what is transient enclosure vltage , very fast transients, very fast transient over voltages
for 750 kw LT load what will be the ht kva
What is resistance reading of earth copper rod with grid and without grid?
in 1-phase 230v,how in 3-phase 440v. in each phase in between 230v.