what is the procedure to isolate flow a transmitter and
flushing it?
Answer Posted / mohammed abbas
If it is dp type of flow tx,
first if is the 5 way manifold means 2 is isolation
valve,2 is drain valve and 1 is equilizing valve,open the
equilizing valve to make presuure both in HP & LP same and
close the process root valves,then open the darin valves
for flushing it.
| Is This Answer Correct ? | 10 Yes | 13 No |
Post New Answer View All Answers
I am having a Phoenix digital to modbus converter. The o/p of the same is connected to flow computer FB407. But the digital signals are updated only after one minute in the flow computer. what may be the cause of delay in communication? Flow computer is having a scanning period of less than 1 sec.
What should be the main consideration while starting the Rotating compressor when we dont know the cut in and the cut off pressure setting of the pressure switch
Instrument QA/Qc what is the project quality plan?conduit inspection RFI. which documents attache with package?
please send the drdo exam paper
what is o2 analyzer and how it measured ,what is the role of this analyzer in cfbc boiler...
Any body have know try work calculation ???
what is the reset offset and control system in instrumentation
what is difference between fork type and capacitance type level switch. where it is using
Can any one tell me what type of question asked for instrumentation and control interview panel??? pls mail ramashankar.goel@gmail.com
How to convert Differential pressure to flow in TPH
What is the use of temperature compensation?
Explain the difference between plc and cnc?
How you calibrate absolute pressure with the calibration range of 0 to 1000 0C Absolute. Please explain the procedure for calibration.
What is the use of gauge?
䑰ҕ䔈ҕ䖠ҕ䘰ҕ䛀ҕ䝐ҕ䟐ҕ䢐ҕ䥐ҕŹ