What are the tests to be taken on a transformer and
generator?
Answer Posted / amit
For transformer these are the fallowing test should be taken
1) Insulation resistance test
2) Vector group test
3) Transformer oil Break down voltage test
4) Magnetic current & Ratio test
5) Magnetic balance test
6) High Voltage test
7) Transformer winding rasistance test
8) PI Value test
9) SC test
10)OC test
Is This Answer Correct ? | 82 Yes | 10 No |
Post New Answer View All Answers
how to determine ct ratio in ht vcb?
Would you recommend to replace all oil filled cables with xlpe cable for hv transmission with the current technolgy for xlpe cable?
What is the tests required for a 132 kV, 400 kV , 765 kV for a Circuit Breaker and Power Transformer before commissioning ?
How out of step protection relay works?
If I want to replace a 26KW Slip ring Motor with a Squirrel Cage motor & Drive (for a Hoist Application). How can I approximate the Motor & Drive HP required in new Setup.
i want design of D.C.MOTOR 1HP 960RPM AND 2HP 960RPM ITS URRGENT
what is the basic need of domestic loads 1- voltage 2- current
what are the preventive maintanance actions taken for air circuit breaker? please answer me
what is ratio of copper wire size and current ?
What is Surge Capacitor? Why it is use in Generator Circuit Breaker?
two phases with neutral supply can be taken in 3C X 10 sq.mm cable .
What are the various types of rotor used in the alternators?
What is meant by rotor?
how much GROUND & NEUTRAL VOLT maintain in data center.
I HAVE A 50A MCCB AS PER DESIGN LINE WIRE CONNECT UPWORD SIDE AND LOAD IS CONNECTED TO DOWNWARD SIDE TO THE MCCB.IF NOW ANY ONE CHANGE SUPPLY & LOAD(WISEVERSA) WHAT HAPPENS ? DOES MCCB OPERATION OR WORKING FUNCTION NORMAL IF YES THAN WHY THERE ARE MARKED LINE & LOAD ON MCCB.