Answer Posted / vinod
I think question is What is the difference between KVA &
KVAR
Ans: KVA is Apparant power-ie. the usefull power while
electrical energy converting in to other energy.
KVAR is the reactive power-ie. electrical power using to
develop the media (flux) for energy conversion.measuring
KVAR is VxIxsinQ
Eg. Induction motor is working principle.
When 3 phase voltage is applied across the stator,a synch.
flux producing in the air gap and voltage inducing in the
rotor, as per Lenz low motor rotates in the same direction
of field.here the flux is the media and the power using for
devoloping the flux is KVAR
| Is This Answer Correct ? | 6 Yes | 0 No |
Post New Answer View All Answers
Transmission voltage is kept 11KV,33KV,66KV,132KV,220KV due to form factor. What happen to 400KV and 765KV transmission voltage?
Electronic circuit
star delta starter contorl circuit... drawing..
Two liquids hot and cold in two vessels are there and an metal bar acts as a conductor of heat between the two vessels. what happens then. what happens after 24 hrs?
LET ME NOW MORE ABOUT icu and ics for circuit breaker. how we calculate the rating of circuit breaker and i c u and ics values
Name of the relay of low lub oil presuure in DG sets
What do you mean by turns ratio of instrument transformer?
Safety of dry type transformer
why r we using shell transformer for low voltage
Draw a 230kv two-bus bar system showing the following. 1.Two generators (150MW) each connected through one 15.75/230KV transformers 2. 1 outgoing lines 3. Two 230/130 KV transformers 4. BUS PT's 5. CT
wish of these transformer uses oil?
What are the specifications for conducting earth leakage test as per IEC standard?
What is the efficiency during maximum power transfer?
What is meant by reset level of the relay?
advantages and disadvantages of inverse definite minimum time RELAY