If a motor of 8.5 KW with same load and using in both Star
& Delta one by one,then which will take more current in
star connected or in delta connected

Answer Posted / pillay

What is important is, the motor is designed to operate at
what connection and what voltage.IF it is designed for the
other connection and you powewr it the other way you will
destroy the motor winding or you wont get the intended
power out put.
power is always line voltage X LINE CURRENT x PF x root 3
for 3 phase motor, and you cannot change it.

Is This Answer Correct ?    0 Yes 2 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

what is relay what is protection & contact multiplying relays where it is used function in brief

671


Difference of induction motor & servo motor ??

1294


what questions are asked in the interview for the post of an electrical maintenance engineer in FMCG companies?

2138


what is the meaning of osr in transformer.

1539


Describe the test procedure to determine the vector group

1590






what is the series parallel connection of capacitors? and how can we use these application in three phase motors for controlling torque?

1574


How many gap between finger contact in a.c.b. and v.cb.?

734


HOW THE OLTC TRANSFORMER SAVE ENERGY IN COMPARISON TO OFF LINE TRANSFORMER AND IS IT ECONOMICAL TO REPLACE THE OFF LINE TRANSFORMER TO OLTC TRANSFORMER

1702


why need to be maintain power factor for industrial customer?

4077


What is the best thing to protect the motor from running over full current. CT or O/L or pressure transducer at the given pressure rating

1019


What the difference between three phase contactor (coil 110vac) & three phase SSR (control voltage 110Vac)? May I use contactor in place of SSR?

1639


What is fault clearing time for Current Limiting Moulded Case Circuit Breaker?.

1316


Hi Everyone ! My Name is Hakim ullah khan please i need formula of Cable Rating because i want to calculate by self without check any Table Chart... Thank you.....

1241


does any one know where we can purchase insulation oil for high voltage oil filled cables

1845


how to find the voltage's of a transmission line plzz help with pictures i am not able to understand

777