Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

how many types of accuracy class in ct? what is meaning of
5p20?

Answer Posted / ashwini kumar

generally two type of accuracy class 5P and 10P.Here, 5P
indicates that this is the protection type of CT with
composite error of <5% at rated accuracy limit primary
current & 20 is the rated accuracy limit factor (RALF) for
the C.T. i.e. overcurrent = 10*nominal current.

[RALF is the primary current up to which the CT is required
to maintain its specified accuracy with rated secondary
burden connected expressed as a multiple of rated primary
current.]

Is This Answer Correct ?    7 Yes 2 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

what is the problem when i want to close a circuit breaker by local position it closes well.but when i close it in remote position it trips

1618


3phase motor can be used as a Prime mover for alternator.

1605


How to measure power in 2 or 4 or n phase circuit? Please give me a formula.

1926


any body,pls tell me how to done relay coordination ? how to coordinate by TCC curve?how to read the tcc curve?

2284


If Dg set load increase 25%, How much increase fuel Consumption (15 kva 2 cylinder DG set)

2274


bitumar

2311


what is the difference between c power and U power acb breaker

6421


we have earthmat at 110KV substation.we would like to take earth resistance.b some says that by connecting earth megger terminals (C1,P1) at middile point of earthmat (at riser) will cause voltage gradient at other earthmat nods and dont get exat earth resistance.when connecting at end nods will get exat value . is it correct .please explain

2221


When the relative speed between the magnetic fields of stator and rotor does is zero under steady state operation?

1277


What are IR values and what it should be for coil and for insulator

3001


How to calculate the electrical load for a standard telecom BTS shelter and choose the DG set capacity for the same load?

3201


what is thresold of perception

2081


why power factor is important?

10379


What is different between Difnit time and instatous over current relay

2553


For R-L or R-C ckt,time constant formula is L/R and RC respectively and its unit is in sec.Pls tell me the derivation

3291