how to choose the cable rating for load (KW)? EXAMPLE.50KW load
Answer Posted / m.saad
Calclate the load Current
I = p/((root3)*V*P.F )
where I line current, v line voltage
then go to cable tabe
and check the Drateing factors.such as
if this cable underground,free,soil,depth of laying,
ambient temperture, armoed or unarmoed etc.
then calcute the voltage drop
if more than 4%
you should to select the next bigger cross section at table.
by experince for copper PVC cables
1mm take 2.5 AMP
| Is This Answer Correct ? | 32 Yes | 13 No |
Post New Answer View All Answers
Main advantage of auto transformer over two windings transformer is that A it needs no cooling B it uses only one winding C core losses are reduced D it has simple construction
What are the common sources of energy?
What happen if we apply square wave or traiangular waveform voltage to the transformer primary winding instead of sinusoidal wave?
What are the limitations of Kirchoff's laws?
how do u gauge the size of the cable ?for eg. consider a 300 sqmm L.T Cable.How do u determine the size of the cable seeing it pratically?
Draw transformer phasor diagram.(full load,no load)
What is critical disruptive voltage?
Is it required to lay 2 runs of GI wires along with armoured cables from one power DB Machines of higher rating?
we have amp, voltage, kw, length detail then how to calculte copper & alluminium size of conductor of 3-phase induction motor
I HAVE BEEN SELECTED FOR APGENCO A.E(ELECTRICAL) 2008.HOW MUCH WEIGHTAGE FOR INTERVIEW AND WRITTEN TEST.HOW I HAVE TO PREPARE. PLEASE GIVE INFORMATION IF U KNOW.WHAT ABT G.D THIS TIME.CALL RATIO 1:2
WHAT IS THE FUNCTION OF SHORT CIRCUIT MAINTENANCE CT
it is possible to rotate the DG engine dc starter with wrong polarity connections? why?
Can i use the B-curve MCB instead of C-curve MCB
What is VCB? where it is installed at SP. What is SP?
can i use 2000/5A Clamp meter to measure HT cable