if we convert kw into Ampers,which one formula use by
us,pls tell me?
Answer Posted / jaimin
FOR 3 PHASE CKT
KW=ROOT(3)*V*A POWER FACTOR
A=KW/(ROOT(3)*V*POWER FACTOR)
FOR SINGLE PHASE CKT.
KW=V*A*POWER FACTOR
A=KW/V*POWER FACTOR
| Is This Answer Correct ? | 4 Yes | 0 No |
Post New Answer View All Answers
How can i calculate the Breaking capacity of molded case circuit breaker, is the breaking capacity of CB for Diesel generator shall be less than grid supply's breaker ?
Why you are switching off arc protection mcb when you are taking shutdown for lv board.
pre arcing time of ehv breaker
Why the field rheostat is adjusted such that the voltmeter reads 380V
WHAT ARE THE DATAS REQUIRED FOR PROTECTION AND METERING AND CONTROL AND LOGIC PREPARATION,HOW TO STUDY THE PROTECTION AND METERING?
1. What is maximum permissible distance between smoke detectors ? 2. How do we decide number of smoke detectors required in a large office, warehouse, hall etc ? 3. What should be maximum height of smoke detectors ? 4. Where do we use heat detector, optical smoke detector, temperature sensitive detector ?
What is the effect on power factor, shown by a trivector meter; incase of reverse phase sequence. If the power factor of a system is lag what meter will show in case of reverse phase sequence connected to the meter. and What in case of lead.
What are the application of filter?
how ceiling fan worked?
use of choke in APFC panels
How to calculate cable size by using load.?? Any formula...
What should be the magnetic balance test values for a 3 phase delta/star connected single primary dual secondary winding transformer (90 MVA / 2 X 45 MVA TRANSFORMER)
12.5 tons a/c is their how much kva generator can recommend to the customer.
should %impedance be high or low in a power transformer? if so why?
How to calculate energy stored in a capacitance