what is difference between power & distrubution
transformer ?
Answer Posted / sagar sethi
TRANSFORMERS RATING MORE THAN 1600 kVA ARE COMES UNDER
POWER TRANSFORMERS.
TRANSFORMERS RATING UPTO AND INCLUDING 1600 kVA ARE COMES
UNDER DISTRIBUTION TRANSFORMERS.
THESE ARE SPECIFIED AS PER INDIAN STANDARD 10028 (CODE OF
PRACITICE FOR SELECTION,INSTALLATION AND MAINTENANCE OF
TRANSFORMERS PART-1, PAGE NO-4).
| Is This Answer Correct ? | 7 Yes | 0 No |
Post New Answer View All Answers
Define coil span?
What is bridge rectifier and explain with details
What is effect on in zone and out zone fault if CT chosen for phase side is Vk/2<5mA and Neutral side is Vk/2<15mA on REF protection of Transformer
HAI SENT HPCL APTITUDE QUESTION PAPER, MY EMAIL ID IS angus_eee04@rediffmail.com,angus_eee04@yahoo.com
What are the necessary solutions needed to be carried out on a malfunctioned earthing mechanism of a VACUUM CIRCUIT BREAKER.(TAMCO)
what is the difference between dry and wet type of 132kV terminations. which one is durable
if main CT is of ratio 50/5, and meter CT is -/5 what will be overall multiplying factor of meter.PT is 11000/110 .
What is the height of DA, DAL, DB, DC & DDE tower?
There is any especial requirement for motor to drive through with VFD?
A 400KVA transformer has 400 Hz frequency. If the frequency is changed to 50 Hz, then what will be the new KVA rating?
Can anyone tell me some hints about what type of questions are asked by the interviewer by an Electronics engineer when company is installing an IPP and wants a team of engineers?
Explain about 3 phase motor fault current calculation with examples?
What are the difference between CT/PT operated Meter and RRAMR Meter for HT/LT application?
How you will determine the volume of oil in a particular Distribution transformer.
At what factor resistance r of a conductor depends?