how is classified voltage level in generation,transmission
& distribution system?,
Answer Posted / ramanjaneyulu
genaration:11kv
transmission: 400kv-33kv
distribution:11kv-415,230v
| Is This Answer Correct ? | 3 Yes | 0 No |
Post New Answer View All Answers
How does cost of generation from hydropower plant compare with other sources of electricity?
I don't understand why when we connect high voltage source in DC to electronic motor , we must add capacitor and resistor in parallel ? (I know that we use capacitor because we want to absorb the current that in the first second electronic motor in opposed with current course produce. ) what are the feature of Resistor and in such situation ?
how to introduce yourself
where is the need for short circuit test for 3 see is required and why? can you explain in brief with application
witch pump used in wtp
why 5kW motor becomes unbalance if its relay trip 1st time and its set value is 7.0 A
What is the maximum percentage voltage drop (vd%)for a motor control center
how to select electrical equipment such as fuse,dg,transformer,motor,msb,wire,cable as per the connecting load..please mention any books to design,take licence
i need the curve duty cycle and amper for (150 kva @50% dyty cycle) transformer turn ratio :19 and vin 400
why do we not use equivalent voltage source in negative sequence equivalent ckt.
I Need standard operation procedure(SOP)for 500kva Oil type transformer oil filtration & Procedure for IR value checking.
substation+ plc system
As you achieve greater success with the company after some years, Will you like to be a share holder in our company?
How much load can be taken for chiller from 1500 kva transformer
Hello sir i m student of gtu .what is idp.