Whats the type of current and potential transformers?
Answer Posted / c.hari balakrishnan
Instrument transformers (potential & Current)used for
protection and metering purpose...Current transformers
which is used for protection is normally 5P20 class,
for differential protection i.e, PX class cts & Metering
0.2FS5 class Cts whose saturation value is very less...
For Voltage transformers 0.2 & 3P class for
metering,Protection...
| Is This Answer Correct ? | 4 Yes | 0 No |
Post New Answer View All Answers
1.Can we use 6.6/11KV 300sq mm xlpe 3core cable for LT use (415 Volt). 2. If we use it for LT then what is the current rating
explain working principle of earth leakage relay
i completed my DEEE. and i want to electrical c license. how to get it..?
it is possible to rotate the DG engine dc starter with wrong polarity connections? why?
neutral earth resistance testing is it possible for transformer while in load condition
WE ARE PLACE A NEW 75 KW MOTOR FOR JPF.IT IS CONNECTED IN M.C.C. WHEN WE ARE STARTING M.C.C.INCOMER IS TRIPPED.THEN WE ARE CONNECTED IN P.C.C WITH A MM30 RELAY PROTECTION THEN WE ARE STARTED MOTOR WILL RUN SMOOTHLY.
what is the difference between ups & inverter
is there any lightning by passer is arranged in ship like buildings?
I use 20 nos led tube 4feet, in pathway 100mtr approximate, so what size cable i use for lighting
Load break swicth maintenance procedure.
According to IEC60034-14, When the vibration monitoring system required for motor Bearing. above which KW, it is required? and for what type of bearing the vibration probe is provided.
how external lighting design? please give examples?
i have install 750 kva distribution transformer at my site and want to do neutral earthing. what calculations should i follow to determine earthing conductor material and size?
What is earth?
what is the purpose of slope in the differential relay?why we are using two slope?but in busbar differential we are using only one slope.why?