Do you know how to measure the earth resistance?
Answer Posted / sandesh
To find the earth resistance we basically need to do the
resistivity test of soil which is symbolized by rho.Now as
per IS we need to have mutual earth resistance below 1 ohm.
so to find the earth resistance for different type of
earthing i.e. plate and pipe we need this resistivity which
vary place to place. for a detailed derivation for both
earthing method and calculation for resistance by one
earthing please refer IS 3043
| Is This Answer Correct ? | 0 Yes | 1 No |
Post New Answer View All Answers
what is the effect of un-synchronized power.
In Dyn11 power transformer if any one of the 3 phases connected to earth in star connected side then please explain effect of the current flow in delta connected side of transformer.(In this case if one phase is shorted to ground in star connected side then we observe the current flow in two phases only not three phases in delta connected primary side. Please explain why it is so?)
What is the emf equation of a transformer?
The 3 phase 400 hp 440 volt slip ring induction motor do not take one phase amps why ? The motor is running good condition
why we permissive overreach in distance protection.where it is applicable to use in long r short lines
What is size 00, 01, 1 etc., in HRC fuse types?
please give me all the Alarm .Trip ,Safety Relays & Conditions of Diesel-generators mail me on ashokbabunhce@gmail.com
what is meant by residual over voltage & residual earth fault ?
Is there any Institution for giving M-tech in Electrical engineering for those who r in service? Give the details please.
How to select a contactor? How many types of contactors are available
How to calculate KVA/VA rating of PT or CT from primary & secondary voltage or primary & secondary current?
is ac supply can store
What is current divider rule (cdr)?
how to calculate the surge level of surge suppressors related to the SF6 cicuit breakers?
why dc is used in control circuits for MV & LV switchgeras instead of ac