Answer Posted / sukhvinder
PID : It is punture insulator detector.
Working : on energised line these PID is moved on insulator
string which measure the voltage gradient against each disc
and from there we can find the punture insulator through
graph.
Is This Answer Correct ? | 9 Yes | 6 No |