adspace
What is C.T, why it is used and what care should be taken
for that while connecting?
Answer Posted / dixit
CT means current x'mer. in actual field high amount of
current in turms of KA so measuring this current is
difficult & also relay current is also less.so, for
reducing current (pri.-high current & sec.-1A OR 5A)CT is
used.
care must be taken that always CT sec. are shorted because,
at sec. less current and high voltage is present. if it is
open than this high voltage affected field operator.
| Is This Answer Correct ? | 11 Yes | 2 No |
Post New Answer View All Answers
Draw a SLD for main panel for school having connected load of 1200kw and emergency generator 200kw.also show the increase of additional load of chiller 225kw in the lv panel indicating meter postion size of transformer ,cables and capacitor bank.
CBCT selection
What types of CMOS memories have you designed? What were their size? Speed? Configuration Process technology?
DRAW ACIRCUIT DIAGRAM OF 100 KVA 415V/55-0-55V DELTA TO STAR TRANSFORMER
what is a reactive power? what is the relation with power factor?
i karmveer bharti persuing b.tech . plz send me syllabus and name of reference books. for preparation of section eng.
Enlist four components of electrive drives.
I am apply the AAI. So i want electrical sample question paper in technical with answer my id is vijayjobsmart@gmail.com
Draw the vector diagram and condition for the following: 1) Dyn1 2) Ynd0 3) YnYn0
Why neutral point is consider as zero potential?
why lightning arrestor are made in two stack of insulator but why not cvt
I have 2500KVA transformer delta/star,13.8KV/380V provided with LV 4000A breaker. Already I have 2300KW motor feeder with a full load 90%. Is it possible to connect another 1600A from that breaker? If so how the calculation is done?
can i able to get bhel previous exam question paper?
Can Anyone Answer anyone of these ? Q1) why direct SOLUTION of Load Flow Studies in Not Possile ? Q2)Why majority of Buses in power system are load buses Q3)Why one of the buses in Power system is taken as reference bus (slack or swing) Bus ? Q4)Bus Admittance Matrix is a sparce (means it contains some zero elements ) matrix , give reason
can you send me the placement papers of electrical engg. from companis like NTPC,DRDO,IOCL,HPCL,BPCL etc.?If,plz send as soon as possible.Thanks.