Why machines are avoided to work is saturation region of B-
H curve?
Answer Posted / iamdon
This is done for AVOIDING THE HIGH MAGNETIZING CURRENT
requirement as explained below.
The magnetising current is the amount of current required
to force the working flux into air gap and meet the core
loss.The magnetising current is directly proportional to B
(average).In the case of magnetic saturation,the value of B
becomes high.So we require more magnetising current to force
the same amount of working flux into the air gap.More
magnetising current is of course not desirable because it will
create heating problem.
Author:arbelectbit@yahoo.com
| Is This Answer Correct ? | 7 Yes | 0 No |
Post New Answer View All Answers
Explain how you can give the overload setting to any Motor Protection Relay for a HT motors with formula and example?
What are the various types of BUSBAR Schemes? explain each
Why we are using Isolation Power Transformer inplace of commercial power transformer? What's the difference between them?
Can RCD's used to protect the VVVF drive if not why.
If any one's require of phoenix contact like( relay , termilnal block , surge protection device ) , product please contect me 09878206357 chetan verma
ACCORDING TO IEC WHAT SHOULD BE THE MINIMUM HEIGHT OF G.I. STRUCTURE OF CT, PT, ISOLATOR, LA?
what is the meaning of osr in transformer.
what is electrical machines
Please, if 1kw is equal to 1.25kva; how then do I know how many kva in 7.5kw?
i have applied for the post of RRB section engineering chennai board please send me previou papers and solved answer. my mail id jagarapusrinivas@gmail.com
which is better to use svc or synchronous condenser why ?
1 Ton is equal to how many watts?
How to configure the drives in PLC, through Profibus commnication. And to how to address it?
In Power Line Communication (PLC) the wave trap is used to block communication signals from entering neighboring lines. My question is this: Why do they allow for different filtering arrangements on these wave traps? Isn't it always going to be a low pass filter since we want the power frequency to go through, and the comm signal blocked?
what is mean by restructuring power system?