what will happen if we give a dc supply to a transformer.?
Answer Posted / mayilsamy ranganathan
When Dc supply is given to primary of transformer it draws
heavy current from the DC source due to absence of back emf
and burnt out.Because the dc current not varying with time
it has constant value throught the period.
(AC is given to transformer the sinusoidaly varying
current creates a sinusoidaly varying flux ,this flux cuts
the stationary primary coils and creats a back emf,
(statically induced emf)this back emf opposes the applied
voltage source to drive current(Lenz law) so current is
limited by this back emf hence no overdrawal of current
from source,this is not happen while applying dc)
| Is This Answer Correct ? | 9 Yes | 1 No |
Post New Answer View All Answers
what is the difference between active power and reactive power and apparant power in practical as well as theoritical
What is the rotor frequency of 10 Hp 1440 RPM 50HZ 415V ?
What will be result if we connect LT votage to the terminal of HT motor?
which types of relay used in acb and vcb?
What is the meaning of HT Trivector Meter ?
i want design of D.C.MOTOR 1HP 960RPM AND 2HP 960RPM ITS URRGENT
What happens if the negative to earth voltage is greater than positive to earth voltage in the battery of substation?
What is a slack bus?
Is it true that in the 3 phase transformer, the limbs of the core are at 45 dgrees to each other. if true, why?
What is the role of Dedicated earthing in UPS System?
What is time response of the control system?
The efficiency of a 100kva transformer is 0.98 at full load as well as half load , for this transformer what is the Copper loss at full load ?
What is knee point voltage?
what should be the no load current for 3 phase ac motors ranging from 5 kw to 1000kw?
why does rotor rotets?