what will happen if we give a dc supply to a transformer.?
Answer Posted / nithi
ANSWER:Nothing will happen.But fuse will blown off.
EXPLANATION: While applying DC voltage to the
transformer,there is no induced EMF in the primary &
secondary wdg.(except during switching period, both ON&
OFF).so,the transformer will draw high current from the
supply which detoriate the winding insulation & cause
transformer to burn.But actually this will not
happen .Becoz,the fuse will sacrifice itself to protect
transformer from high current.
| Is This Answer Correct ? | 8 Yes | 3 No |
Post New Answer View All Answers
Match the following a)(X'+Y') b)X'Y' C)XY 1)NAND 2)NOR 3)Carry
power transmission pole used one support , that only for support or earthing
Keywords: Die, Card, Coin, B/N 2 To 12
Explain M Var? Which types of problem occurs when reactive power increase at the time of full load of plant and at the time of synchronize of plant?
How to calculate the value of earth capacitance in a transmission line.
How can we checked Killo Watts of Motor & Alternator?
bus bar design conditions and sizing pls tell me quickly
for 5KW resistive load can anyone please suggest me whether to go for UPS/Inverter or Generator depending upon cost calulations
working function importance of mdc meter
According to IEC60034-14, When the vibration monitoring system required for motor Bearing. above which KW, it is required? and for what type of bearing the vibration probe is provided.
What is meant by reset level of the relay?
how the B-H loop obtain under the static condition
there is an alternator 480 k.w, 400v,50hz, 4-wire running on load having leakage alternator body earthed current 38 A. is it within acceptable limit? if yes then give reference if no then how to bring within specified limit
What is the difference in calculating size of AC cables compared to calculating size of DC Cables? Usually DC Cables are larger than AC Cables although they have the same ampacity. Why is it?
how calculated Transformer losses.