what is the difference between synchronization and paralleling?
Answer Posted / tareq harb
synchronizing is making phase, voltage & frequency the same
or with small difference between generators.
paralleling is sharing the load among all this generators.
so synchronizing is done before closing the ckt breaker but
after closing it parlleling process starts and all above
mentioned parametrs stuck together.
| Is This Answer Correct ? | 71 Yes | 4 No |
Post New Answer View All Answers
why are installed water leakage detection system data centers & server rooms
What is boucholz relay and the significance of it in to the trformer?
What are the classifications of oscillators?
what is the eight bit unit?
What is corkscrew rule?
Where I can get the sample question for post of Junior engineer electrical-II For RRB Bhubaneswar.
if the armature current in a dc generator is ac ( sinusoidal ) why doesnt the sjhape af armature mmf a sinusoidal (ni) ? armature mmf in case of a dc machine is triangular.
If VFD is On but no starting commond on it. so how many outpout voltages of VFD
ii) A shunt motor supplied at 230V, runs at 900 rpm when the current is 30A. The resistance of the armature is 0.4 ohms. Calculate the resistance required in series with the armature to reduce the speed to 600 rpm, assuming that the armature current is then 20A. [12]
What is a commutator?
i have faced a problem in ro plant grunfos make bm30type pump it is 22kw pump. We start this pump using siemens 3rw 4423-ibc44, 30kw softstarter but this soft starter will frequently failier so we planed to change dol starter. So pls tell anybudy its possible or not.
how to calculate the cable current ratingand and how much of distance the rating will be ok will the distance is incresed what the action we take
Q.1:What protection will be used on HT and LT side of 33/0.4 KV, MVA transformer. Indicate capacities of protective device to be used. Q.2:Which types of back-up protections are used in the power transformers? What do you understand by the term over travel in the relay? Q.3:How star and delta connected winding transformer are provided from earth fault
acb(AIR CIRCUIT BREAKER)NOT CHARGING AUTO