what is the difference between synchronization and paralleling?
Answer Posted / tareq harb
synchronizing is making phase, voltage & frequency the same
or with small difference between generators.
paralleling is sharing the load among all this generators.
so synchronizing is done before closing the ckt breaker but
after closing it parlleling process starts and all above
mentioned parametrs stuck together.
Is This Answer Correct ? | 71 Yes | 4 No |
Post New Answer View All Answers
What is an Air COmpressor
checking procedure of capacitor based motors.used in fans etc?
What will happen to the protection and metering, if the polarity of a single or two PT/PTs in three phase system is reversed? Please provide reference if any.
What is the difference between isolators and electrical circuit breakers?
What do you mean by transformation ratio of instrument transformer?
how to wiring it with contactor and timer together
I want d.g.set our company
What is meant by sag?
hi friend i am going too attend for hpcl in this month please help me by sending written test question papers i am in the stream of E.E.E
volts=230 c=10mf a=??
If not into production, how far did you follow the design and why did not you see it into production?
What is the universal motor?
What are stable systems?
In Air circuit breaker LSIG protection unit is used. Without fault in cables (2 runs 3Cx150Sq.mm Copper, 1Kv grade, XPLE armored cable IR value is more than 550Mohm @ 500V Megger) and load section Long time Overcurrent protection is triggers and trips the unit. We changed LSIG protection with new factory tested unit. Even then fault is persisting. Please suggest the possible causes
What is method of calculating the fault current for a MDB, 50KW, 3PH, 415V, 50HZ?