how many test is necessary for 27mva transformer.
Answer Posted / sumit shukla
short ckt test measure eddy current loss,hystresis loss
open ckt test measure omhic loss
back to back test
| Is This Answer Correct ? | 0 Yes | 3 No |
Post New Answer View All Answers
Describe the colour rendering properties of i) tungsten filament lamps ii) tubular fluorescent lamp
what is earthing transformer? draw the winding dia.of earthing transformer.
Is it possible to implement Restricted Earth Fault protection for a transformer without neutral CT?
what type of questions are asked and howmwny questions belong this catagory?
what is mean by NPS (Negative phase sequence)fault? what is the difference between EFR & OCR faults?
Define transfer function?
What is the difference between the transmission line and distribution line?
how to calculate power consumption in slip ring motor at different step
What is Phase to Phase clearance for 800V System Operating Voltage as per IEC61439
how to compare with Relay settings for HT< panels, RMU panel, and PSS CSS transformer?? 1) Load amps, 2)Tripping time, 3) CT ratio, 4)Cable size 5) Transformer KVA rating 6) transformer full load amps
we are having 110 Kv,250mA Electrostatic precipitators for coal fired boilers. what will be static voltage and current after discharge and what time it will remain before earthing?
Why we find the sensitivity for the CT's to check?
What is main cause of cable's terminal point burned in Lug on high temperature although lug and cable selection is ok as per stantard and also tightness is ok as per situation. so please take in deep and tell correct answer thanku.
How to calculate the input cable rating for 10kva ups (3phase input and single phase output and also 3phase output, battery rating 65Ah)provide the formula also.thnx
give me applications of sequence bridges . (used in 3 phase un balanced systems)