Answer Posted / rated kuldeep
AC transmission is used as compared to DC because for
following reason... AC can be transformed to low current
high voltage configuration using transformer. Conductor size
required will be less and hence more economical...... 2nd
reason which is main reason is AC is bidirectional hence has
ability to move in both the directions ...
DC can be transformed according to need but costly
rectifiers are neede heence for buulk power transmission ac
is used... correct me if wrong.....
| Is This Answer Correct ? | 23 Yes | 3 No |
Post New Answer View All Answers
IN 1000kva transformer where the oil and winding temperature sensors is connected
WHAT IS MOBILE SUB-STATION? & REALLY BENEFIT IN INDIA
what is the safe meggar values for motor, transformer HT, LT and Cables? IF we want to replace I/C bay at our 220 kv substation which is of 140 mw load capacity bay to be replaced by 400 mw capacity bay.other than CT(1200/1) what are the other equipment i have to replace. why we generally use 3.5 core cable or in other word 1/2 core for neutral and also confirm me that in balance conditiob(3 phase)current in neutral will zero
How to check the cable fault / hv test of transformer cable.
write down the formula of cable size in RM if current is 50Amp.
State angle criterion.
why we permissive overreach in distance protection.where it is applicable to use in long r short lines
What is dc current source? Differentiate between ideal and non ideal current sources?
What is process of anneling transformer core
Explain different types of d.c motors? Give their applications
How to derive detailed design of Suitable bus Bar for 100A for 6.6KV?
What is the efficiency during maximum power transfer?
Wind mill
how to calculate vfd o/p voltage by frequency
What is the meaning of loop in transformer