Please send specifications for 1000KVA dry type transformer
or where I can get the specifications?
Answer Posted / sree
specification means all the details like,dimensions of the
core, winding size,%impedence,vector group, protections
required etc.,as like a oil cooled transformer.
| Is This Answer Correct ? | 2 Yes | 1 No |
Post New Answer View All Answers
Define sensitivity?
we are having 15kw and 3kw motor both can run in same time , instead of using copper we are using ug aluminium cable , 35 sq.mm is suitable for its current carrying capacity..?
What do you mean by lighting transformer?
defult setting in p220 micom motor proction relay for 11kv,640kw,f.l.a.-40a,1440rpm ht motor?
primery try cell?
1 “earthing” for bonding of equipment and circuits to common plant earth electrode potential, 2 “protective earthing (PE)” when this bonding is required for personal safety provisions 3 “grounding” for interference suppressing bonding of screens, sys-tems with ground level 4. low-impedance earthing ? 5.primary earthing system and secondary earthing system what is that? 6.earthing electrode or mesh net earthing electrode ? very confusing , simple but very informative help required ? i will be very very thankful to you guys.
Can anyone please provide me details of MCCB/Contactor/SFU rating calculations for a motor feeder..for example 50 kw.. not from type-2 cordination chart. i want manual calculations..
why do we put a transformer on soak before loading it
How to calculate loses in transformer of 160 KVA ?
I am designing new project sub station with 220 kV / 11 kV, 40 MVA capacity. This project have many recifier sets, which can generate 3rd harmonics. Now I have to select vector group of This transformer. To minimise 3rd harmonics, what care should I take in selection of Transformer Vecrtor group? If it is Y-Y with open Delta tertiary then what should be the rating & voltage of Tertiary Winding?
What Is Connection APFC Panel In Compony.
What is the formula of frequency ?
how much excitation voltage required to generate 1mw power?
Please tell me the formulaes while designing a substation for power Calculations in designing a 33 KV Substation?????
If I want to buy a new Xformer for my plant what are the main parameter will I need to check?