Answer Posted / vaibhav kr. pathak
the outer strand flux links external surface of the
cable,while internal mutual flux links both external &
internal surface of the cable thereby increasing the
inductance of the innner core of the cable which leads to
hindrance in flow of current in internal section of the
cable & hence concentration of current is higher on outer
surface called skin effect
Is This Answer Correct ? | 7 Yes | 0 No |
Post New Answer View All Answers
What is difference between SMC supportg and Glass Fibre Reinforced Plastic Support.
why do we have spikes enough to burn electronic boards, when generators are not grounded
what clearance required for 4.5 mva dry type transformer?
what is the importance of earthing system on the generators big capacity and small?
how does it help for selection of a transformer.
Why neutral is not used in three phases dol starter
How to resolve if Diesel generator stop while running ?
HOW TO CALCULATE HV CABLE SIZING?
In CTs tan delta point should be earthed , what is the reason behind it?
what size steel armoured cable is required to support 1500kva capacity. would 70mm squared be enough or would I need 90 or 120mm squared 3c plus earth
In ACS 1000 drive we are using 12 pulse converter,why don't use 3 pulse converter.
what is the illumination level required for child play area?
what transformer we used normally and upto which kva?
Different STANDARDS (BS, IS, IEC etc) gives different informations on CT specification. How they correspons w r t each other (i.e I mean to say BS provides "knee point voltage" but IS does not, then how can i select CT)
Difference between on line capacitor and Station type capacitor