Answer Posted / hardik vyas
30 mA ELCB is used for human protection. Cause the current
which is passing through human body, exeeds 15 mA then it
can cause serious injury or even fatality. Here if your
ELCB is 30 mA, it will trip before it reaches 15mA...
| Is This Answer Correct ? | 47 Yes | 15 No |
Post New Answer View All Answers
A jet of fluid strikes a plate What was the force required to counter it?
what is meaning of sympathetic tripping with respect to relays and give the values for current carrying capacities for copper and aluminium cables from 16sq mm to 500sq mm
how to calculate distance between busbar supporters for LT panel, what are the factors influencing in this design
how point on wave controller works.
If more than rated DC voltage appears across trip coil of the breaker, what will happen? e.g. in 110V DC circuit system, if voltage across battery terminal showing 121 V
In the ACB breaker capacity is 2000Amp but this each phase taken 1250 But total beldibg load is 600amp or 700amp watt is the problem
how is capacitor bank look like
what is meant by star/delta voltages as 440/220 in a 3 phase induction motor, and why it should be connected on STAR IN 3 PHASE SUPPLY
CAN CU XLPE/PVC CABLE BE USED INPLACE OF LOW NOISE SCREENED CABLE? KINDLY GIVE REASONS
How much inductance or resistance require as a starter in series with induction motor of specific capacity(e.g. 5 hp) ? What is formula for it ?
trasnfarmaer core make
WHAT IS MEANT BY INSULATION CLEARANCE IN VACCUM?
when we have to purchase the transformer by own i.e how much load will preferred HT connection?
Write the current equation in series RLC circuits.
I need the list of Universities who have summer intake for BS degree in Electrical Engineering.?