Can we connect more than one NGR at a time of different
rating of generators. what is advantage or disadvantage.
Answer Posted / sudheer
If we connect two NGR at a time , there is a possibility of
producing circulating current. and the generator will tripp
on circulating current fault. so normally we disconnect the
neutral of first generator and then we connect the other
generator neutral with NGR.
| Is This Answer Correct ? | 6 Yes | 2 No |
Post New Answer View All Answers
WHAT IS LOAD CELL
in dc shunt motor if field winding is shorted then
what is a synchronizing lamp ?
What are linear and non-linear systems?
how to calculate the conductor size for certain KV transmission line and distribution line?
a 100mva,400/200v transformer has leakage impdce of 10% draws a steady state line currentof---------------
What is milivolt dop test in Busducts? What is its significance & procedure to do the test?
dear sir/madam i want to get some knowledge about RRB EXAMINATION(section engineer) 1- what is minimum cut off 2- wht portion is major portion . 3- can any body provide Sample paper. thanks & regards ashish
Why armature rheostat is kept in maximum position?
I meggared my 2c*70 sq mm AL AR XLPE cable. its one end show 50 M ohm . is my cable is safe for laying. I have only one phase and neutral.
critically criticize the application of ring main unit in power system
Explain different types of d.c motors? Give their applications
what is meant by star/delta voltages as 440/220 in a 3 phase induction motor, and why it should be connected on STAR IN 3 PHASE SUPPLY
In radial network the source is fed from 1 end both ends at central
How can calculate the earthing strip of Copper/GI for rating of 30kV,discharge current 10KA Lightning arrester.