what happenes if two voltage source connected in parallel
will be connected to load.
Answer Posted / z_hosen
Good question..
If u want to connect two voltage sources at first u have to
follow some rules like
1. Phase sequence should be same
2. Frequency should be same and
3. Voltage should be same
if any two or more voltage sources which don't follow the
above conditions then current will be Inter circulated
between sources and if the voltage range is more then the
system will be damaged..
thanking u..
z_hosen@yahoo.com
| Is This Answer Correct ? | 54 Yes | 4 No |
Post New Answer View All Answers
What size cable (based on voltage drop) is required to supply a 40 A three phase boiler if the wiring system is 75V single insulated cables installed in non-metallic rigid conduit 56m from the main switchboard? Voltage drop in the consumer's mains is 8V.
We need to current density & short circuit calculation at 65kA for aluminium & copper busbar.
Define Electrical Insulation and examples of Solid,Liquid and Gaseous insulating materials?
what is frequency response?
Do closed loops systems require manual input?
What will happend if given Vfd out put to step up transformer
State kirchoff voltage law?
What magnetic circuit is formed in berry-type constructions and why?
please send me previous year questions of jspl through which i could prepare myself for the test.
how do we calculate length of starting time and repeated starting of a direct online starter?
What is a surge supressor why its is used in synchronous generators
How to decide DO set rating of Transformer?
in parallel operation of power transformer why the distance between power transformer and capacitor bank feeder is necessary to know
Atwhat condition reverse power relay will act?
mccb service sittings be done?