what is the difference between elcb,rccb,mcb.
Answer Posted / deep
As said by Naveen -
MCB = Miniature Circut Breaker.
i.e in case of over load (higher that the nominal current)
is drwan by the load the MCB trips (opens the circuit).
However, Naveen is wrong in defining ELCB & RCCB.
ELCB = Earth Leakage Circuit Breaker
RCCB = Residual Current Circuit Breaker
Both ELCB & RCCB are synonymous; the function being only
earth leake protection (and no over load protection)
i.e ELCB a.k.a RCCB trips in case there is an earth leakge
on the load side.
| Is This Answer Correct ? | 93 Yes | 12 No |
Post New Answer View All Answers
What are the various types of rotor used in the alternators?
how to calculate the mesh earth network resistance in such substation, is there any recommended resistance values with references , thanks!
Efficient electrical earthing in hard rock area
What current position are you holding in your current company?
If any one's require of phoenix contact like( relay , termilnal block , surge protection device ) , product please contect me 09878206357 chetan verma
Do closed loop systems require manual input?
How to calculate no of EARTH PIT? Describe the formula as per IS standard?
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
State and define ohm’s law?
is it possible to say motor horsepower number without seeing name plate(when name plate damaged)
What is contract demand in solar system?
what transformer we used normally and upto which kva?
explain which quantities change in the starting and the and the running condition in induction motor
The power supplied to a 33microF capacitor from a 120V, 60Hz source will be
A Question Like A Wire Is Wound Whose Resistance Is Some 132. 44647 Ohms. If A Voltage Of 30 mv, 296 Ma Current Is Applied To It What Is The Resistance.