what do you mean by star connection?
Answer Posted / sareer ahmad lone
Star connection is that connection from where we can take
the neutral point.If you take three coils in a transformer
similar ends are joined together to form a common point
which is called a neutral.We can earth the neutral point.
Normally for bigger transformers like 66kV or more the
connection is star/delta,and the cost is less because the
higher the voltage the more the insulation you have to
use,so if you use a star primary you can degrade the
insulation towards the neutral point,then using less
insulation.Hope the answer is correct
| Is This Answer Correct ? | 14 Yes | 4 No |
Post New Answer View All Answers
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
At full load wat is the motor p.f And at no load will is the motor p.f?
what is W.T?specify the acceptable range?
What is the tube exial fan?
Explain different types of d.c motors? Give their applications
Can RCD's used to protect the VVVF drive if not why.
if field breaker of generator is closed prior to its rated speed on a power generating unit. what will be the effect on generator, unit transformer and starting transformer.
Electromagnetic torque developed by the motor is compared to shaft torque. A less B same C depends on motor design D more
If increased the frequency up to 1000 then what changes shows in voltage?
how to select overload-relay for perticular motor 1.for D.O.L. starter 2. for Star-delta starter ????
why does connected a indutor with mnsformeretering core of current transformer ?
what happen when power factor of 2 parallely operated transformer become equle?
How to calculate the sag of OPGW during stringing???
What are the advantages of nichols chart?
What is referred to the electron in the outer orbit?