Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

what do you mean by star connection?

Answer Posted / sareer ahmad lone

Star connection is that connection from where we can take
the neutral point.If you take three coils in a transformer
similar ends are joined together to form a common point
which is called a neutral.We can earth the neutral point.
Normally for bigger transformers like 66kV or more the
connection is star/delta,and the cost is less because the
higher the voltage the more the insulation you have to
use,so if you use a star primary you can degrade the
insulation towards the neutral point,then using less
insulation.Hope the answer is correct

Is This Answer Correct ?    14 Yes 4 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

how to test the turn ratio of 3 phase transformer using volt meter shoe the curcit diagram.

2461


What are the section criteria for cables. Now everywhere XLPE power cable is used or PVC is also used?.

1674


Pl.brief me any electrical major fault you have rectified.

1961


a 230v transformer with step down ratio 19:1.it has 2000turns on primary and rated 25va calculate max primary current no of secondary turns volts/turn

1547


What is the difference between the impedance percent and impedance voltage ?

2215


What is icu and ics in Acb and how many time icu or ics passes from breaker?

1559


how to prepare the technical test

2094


how to calculate sizing of NGTR (Transformer rating,Loading resistor value and Current rating of resistor) and what is the X/R ratio. Details : 11kV,Capacitance 1.73532 micro farads,40kA for 1sec.

2281


what are the reasons of CT circuit faulty in busbar protection scheme?

1479


How would you calculate power loss in a resistor?

1079


what is the electrical?

2117


what could be the RMS value and average value of a 4 phase sine wave?

1887


what will happen if earth of 33 kv cable (earthed system) is not connected to earthing pit?

2039


What is the efficiency during maximum power transfer?

1245


what is formula to cal cute earth pit numbers and size of earth strip used in earthing?

2221