What is the difference between Relay and Contactor
Answer Posted / vikrant patel
First Clear Relay Means
1. Protective relay
2. Control Relay.
If talking about Protective relay (Example: over current
Relay, Electronic motor protection relay..etc)
so protective relay is for Protection of circuit
and functionally different from contactor.
they have only potential free contact at output which can
be used in control circuit.
if talking about control relay
1. Power relay (which have Change over contact with high
current capacity)
2. Solid state relay
3. Simple control relay. (Which have Change over contact
with low current capacity call SPDT)
This all relay has functionally similarity with contactor
that they are electromagnetic device (except SSR) but
difference
- relay have changeover contact (NO, NC& Common) while
contactor have power contact NO) & auxiliary contact (NO or
NC).
Main difference is
- Contactor is used to Control power Circuit while relay
are used for control circuit (except Power relay which is
now a days introduce for DC/High voltage application).
| Is This Answer Correct ? | 117 Yes | 11 No |
Post New Answer View All Answers
How to design the no. of ceiling fans required in 5mtr X 10 mtr X 3 Mtr hight room?
11kV capacitor bank of rating 2.4KVAR, is charged with protective relays of only over current & Earth fault &.......without Over Voltage, Under Voltage & Neutral Displacement Relay. Is it advisable??
What is negative sequence over voltage element?
How impulse levels are calculated that for 11kV impulse is 75kvp, for 24kV impulse is 125kvp ?
What are IR values and what it should be for coil and for insulator
how to measure earth resistance of a substation
In synchronization circuit what is the function of Interposing voltage transformer(IVT)and Reverse voltage transformer(RVT)
i have to install a HT panel, what components, I have to use in this and what will the diagram of that diagram,please tell me each and everything.
a battery is having capacity 100AH and 25% charging .if a load taking 10A & connected 6 hour .what is the final condition of the battery.
Can anybody please refer the best and simple book for about Protection relays and in detail of all its protection ?
what will happen if the prime mover on the field excitation of the on-coming generator fails?Explain.
How to do maintenance of transformer feeder.
How to run a three phase motor into single phase........
what's producer of XLPE cable laying in undergroung
How to operate a ac chilar plant?