How can we measure and monitor critical performance
parameters of Diesel Generator Sets, both electrical and
engine ?
Answer Posted / guest
Critical parameters of engine are:
1. Max. torque or breakdown torque
2. max. speed and minimum speed.
3. speed reduction with % of full load.
4.max. working temperature.
5.speed governor charaterestics.
and that of alternator is:
1. starting ampacity
2. max. working insulation/ conductor temperature.
3. frequency variation on % of full loads.
4. voltage drop on % full load.
5. over load capacity
| Is This Answer Correct ? | 2 Yes | 2 No |
Post New Answer View All Answers
Why are lt windings placed near the core?
how was your last weekend.
What is the function of RCBO? What are the different sensitivity ratings & each application?
I am designing new project sub station with 220 kV / 11 kV, 40 MVA capacity. This project have many recifier sets, which can generate 3rd harmonics. Now I have to select vector group of This transformer. To minimise 3rd harmonics, what care should I take in selection of Transformer Vecrtor group? If it is Y-Y with open Delta tertiary then what should be the rating & voltage of Tertiary Winding?
why single CT used in DOL starter power circuit?
what is transformor oil gread
what is KSR type transmission tower? What is LSR type transmission tower?
at work i have a genertor/alternater what is the easyest way to work out if it is dc or ac?
What is the universal motor?
In between UPS out going changer over switch and ups raising main input, both side cable gland producing heat but the cable doesn't get heat,Why?
Why insulation level follows this order? transformer < bus bar < circuit breaker & Isolator < transmission line.
how to meas-our losses for L.T & H.T
can we start slipring motor on star delta like we start induction motor ? if yes where will we connect ?
why industry prefer ht motor instead of lt motor.
why electronic instruments is more favorable than electrical?