why is the vector group analysis done in transformer tests

Answer Posted / fred jabagat

Vector Group can be used as basis in setting the phase
compensator factor for numerical transformer differential
relays, i.e. SEL387.
A 3-Ph Transformer is wired internally in different ways to
produce a desired phase position between primary and
secondary terminals.
IEC standards develop a transformer circuit configuration
and a corresponding vector group code which follows a clock
that represents a 30 degrees shift in every hour.
The CT's of a numerical transformer differential relays are
usually wired with its polarity mark facing away from the
protected winding. Because of the phase shift between the
primary and secondary terminals of the transformer it is
necessary to set a phase compensator factor to the
differential relay so that it will not trip on normal load.

Is This Answer Correct ?    38 Yes 6 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

How do u analyse protection fault when vcb tripping on load

1156


difference between Ac and Dc mcb ????

1116


Should power factor be low or high?

698


What is the distance between each insulator in 33kv transformer and how can it calculate

1748


Why r u using pf panel. what the uses

1495






what is level 2 automation?

2704


What is the function of probe in cro?

635


what is PWM in IGBT and how it works for drive.?

1226


Is there any reason that we get shock on touching phase wire because the earth is at neutral potential? Is there any reason that the earth is at neutral potential because the neutral is earthed in apower station

1543


What is the need of generator relay panel

1513


volts=230 c=10mf a=??

1571


What are the types of excitation system?

1466


some time we open engine breaker 8.0 MW load but plant not trip. and another time engine open 4.0 MW load engine trip why? individually engine breaker open & individually emergency stop why difference?

1307


ELECTRICAL ENGINEER TEST IN FEWA ANY ONE HAVE KNOWLEDGE ABOUT THIS?????????

549


To make a basic instrumentation amplifier, it takes A One op-amp with a certain feedback arrangement B Two op-amp and seven resistors C Three op-amps and seven capacitors D Three op-amps and seven resistors

1522