Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

if receiving voltage is higher than sending ones what will
be the effect of receiver

Answer Posted / krish

A Long Transmission Line draws a high quatity charging
current,if that circuit is lightly loaded then recieving
end voltage is greater than sending end voltage.This effect
is known as FERRANTI EFFECT.

Is This Answer Correct ?    10 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

If we use 250A MCCB as a incomer in Control panel for a fault level of 50kA for one second ,assuming temperature rise from 85 Deg. to 100 Deg , Then what will be the Aluminium Bus-bar size for 250A MCCB? Explain in detail.

2285


In the formula : Knee point voltage = Burden X alf / class, Please inform what is alf? regards Shashidhar M.R.

4128


How select ELCB for 32amp. socket having quantity 12Nos. We have to do this wiring in PLANT. Please Also explain the incoming cable specification.

1826


features of hbc fuses

2354


How much earthing frequency is capable?

1918


I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?

1813


xpression 'document.FrmQF.myemail' [

1951


A 100 kVA , 400 v/250 kv testing transformer has 8% leakage reactance and resistance on 100 KVA base . A cable has to be tested at 500 kv using the above transformer as a resonant transformer at 50 hz . if the charging current of the cable at 500 kv is 0.4 A find the series inductance required . Assume 2% resistance for the inductor to be used and the connecting leads . Neglect dielectric loss of hte cable . what will be the input voltage to the transformer ?

5181


An impedance of 100 ohms resistance and an unknown inductance is connected across the capacitor. The resulting impedance is a pure resistance of 500 ohms ifω = 10^5 rad/sec. calculate the values of inductor and capacitor.

1356


why steady state stability limit is greater than transient stability limit ? How it can be explained ?

2860


how to calculate insulation level of transformer?

1634


why single phase to grd test in HV cable?why not 2 phase at a time?

2224


What is dc current source? Differentiate between ideal and non ideal current sources?

1387


what will happen if synchronous machine rotor fed from single phase ac supply 

1687


What current position are you holding in your current company?

2031