can any one tell me the formula for calculating the power
and unit consumpetion
Answer Posted / mubashar ali
total KW * total runing Hours= unit
for example
5 lamp 100 watt each onload for 6 hour
AC 3000W onload for 3 hour
Motor 5HP (5*746=3730W) onload for 2 hour
than
500/1000 * 6= 3
3000/1000 * 3= 9
3730/1000 * 2= 7.46
total unit = 19.46 * Rs.
| Is This Answer Correct ? | 12 Yes | 0 No |
Post New Answer View All Answers
Is there a standard depth of gravel fill in Substation Switchyard? Please give a design/drawing. Thank you.
How much current will a 5 HP delta connected motor at no load will take?Is tat need a starter
what is vA rating and class of a ct.
can we make a electric generator,which can not use any type of fuel,air,solar,gas,thermal,coal,petrol,etc and able to produce electrical energy (or self electricity generating generator)
What is the meaning of dedicated earthing?
Can anybody tell abt concrete encased earthing or grounding?
If Dg set load increase 25%, How much increase fuel Consumption (15 kva 2 cylinder DG set)
can you please send me the technical questions and aptitude questions of honeywell and jindal steel electrical engg. question paper my e-mail ID is(kkesavanraj@gmail.com)
What are the ratings of VCB, MCB, MCCB, SF6, ACB, and OCB?
How can we choose the rating of submersible motors
In ups static switch if i gives the supply at output end it will open the circuit in stactic switch or not if it will open then how it operates.
is there any chart showing the suitable cable size according to AMP and length ? for three phase motors
what is the difference between online & offline caliberation of KWH meters. Can Digital meters be caliberated
How cable from Kit-Kat to main switch, from starter to motor are designed?
What are the site acceptance tests for power cables, DG Sets, LT panels & 30kVA UPS ?