what do you mean by 1 ton in AC`s

Answer Posted / yash

The cooling produced by melting of 1 ton of ice in a day is
taken as unit of refrigeration (in tons). Now unit of
refrigeration used in S.I. System is KW.
1 ton of refrigeration
= mass of ice x latent heat of ice / 24 hrs

= 900 kg x 335 KJ/Kg ( one short ton = 900 kgs )
------------------
24 x 3600 secs
= 3.4895 KJ/Sec
say 3.5 KJ / Sec = 3.5 KW

that is 1 ton of refrigeration = 3.5 KW

Is This Answer Correct ?    284 Yes 33 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

Why a tesa lamp is glow between two phase?

1605


what is draiv work

1505


how to select the double earth conductor if 21A full load?

1682


what is the terminal voltage of dc series generator running at rated speed at no load?

6607


How do we arrive at selecting reactive capacitance value as 30% of h.p rating of motor?

1444






what is the calculation formula for motor starting torque,running torque, running torque.

1301


ANY ONE TELL ME ABOUT generator synchronization panel panel to synchronise 3 gen of 250kva both automatic and manual. 2 gen output vol 415 3ph, 1 gen output vol 400 3ph SEND THE DETAILS DIAGRAM ON THIS EMAIL ADDRESS ayazleo@hotmail.com as soon as possilble best ragrds electrical engineer ayaz mahmood SAUDI TECH

3779


If a current -8+6sin6t is flowing three ammeter, one is a centre zero PMMC meter, one is true rms meter and one is moving iron meter. What are the reading of these three meter respectively?

1744


what is mean by descripiency relay? & wht is its ansi code?

2719


Installation resistance for whole installation of 16 kva & 25 KVA DTRA a) Between each conductor b) between conductor to earth c) installation resistance for each apparatus, each conductor to earth d) earth resistance for the system of earthing

1537


what is the internal working of star delta starter

1734


What is meant by stator?

723


How to calculate the phase to phase clearness of HT /// LT bus bar?????

1671


HOW TO CALCULATE HV TEST VOLTAGE FOR ELECTRICAL EQPT.

1835


Why is it prefer to initiate circuit breaker failure by "86" lockout relay not by "94" tripping relay ?!

1370