in single phase we get 220 volt and in three phase 4420 v
why this
second Ques= in case three phase star conection our
neutrul becom disconect what happan
3 Q=== a three phase house load and have unbalce load on
different pahse diffrent current eg phase a 7A b 8A c
5A and voltage is 440 than how calculate it total load in
kw pl give formula thanks
Answer Posted / deepakindi1
1)In single phase u measure Voltage wrt neutral ie Phase to
neutral(VN)which is phase voltage,
#In three phase if u measure voltage b/w two line terminals
ie b/w R-y or Y-B or R-B it vl b 440v even in three phase
supply if u measure voltage b/w any phase and neutral point
it vl b 220.(Vph=VL/(square Root of 3).
2)A break in the neutral conductor can however result in
wide rise of the voltages between
each phase and the star point if the three single phase
load currents deviate from the ideal
balanced condition. Depending on the degree of unbalance
between the single phase loads, in
the extreme, the three single phase voltages (phase to
neutral) could vary from as low as zero
volts, to any voltage up to the phase to phase voltage.
Irrespective of load balance, the voltages
between phases are not affected by a break in the neutral
conductor.
3) VR*IR*cos(@)+Vy*Iy*cos(@)+Vb*Ib*cos(@)
Is This Answer Correct ? | 6 Yes | 0 No |
Post New Answer View All Answers
what are the components in electrical control panel (for example: 415V, 3-ph, panel to operate utility and 3-ph DG set).
description about dry type transformers
Any one who apply for Ferro Scrap Nigam Limited cn join with me at rajuhalder@indiatimes.com or 09669717028
What will happen to the protection and metering, if the polarity of a single or two PT/PTs in three phase system is reversed? Please provide reference if any.
Who are the manufacturer for Nitrogen based Fire Protectio/explosion prevention for Oil Filled Transformers? India and international both?
How do we calculate the resistance per metre of single core aluminium stranded cable 19*3.25mm sheathed in pvc,at 15 deg C temperature?
why the India electrical supply transmission loss is high when compare to us
what is the difference between skin effect
How we can determine short circuiting current any plant and for example a plant which power generation is 415 volts and plant load is 500 kw.
How can we design a HVAC Plant room which includes AHU,FCU,Chillers,Cooling towers, Pumps etc & how will they work? any Drawing if possible?
which type of amplifiers are used in multimete?
Dg pf .71 i am improve pf 0.80 what capacitor connected in dg how?
what types of cable used in underground coal mining?
What is electrical grounding?
WHAT IS THE DIFFERENE IN ACTION OF MCB,MCCB,RCCB