Differance between power circuit and control circuit

Answer Posted / e.subhash

Power circuit= we deliver or draw bulk power say in power system mw

control circuit: our power circuit equipment is controlling by small range of power .

Is This Answer Correct ?    2 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

How much load can take a 16 mm aluminum cable 3 phase

1268


I have an existing old MCCB. ABB Model SACE, the rating are: Ue = 660 volts, Iu =1250 Amps, 3 poles, Ith (max) =800 amps at 45 deg C. I need a circuit breaker for my 3 phase motors, 380 volts 60 hz. the supplier required the minimum ampacity of the breaker to be 911 amps. can i use this breaker with rating of Iu =1250 amps but Ith = 800amps maximum?

1786


How to Calculate KA Rating of Main LT Panel

1185


What effect does a very low impedance have on the Voltage regulation? On the short-circuit current?

5834


What is the method of estamating of cable, CB,MCB ?

1680






how we explain parallel paths armature winding?

1460


what is high - pot test. what's its use?????

1617


what will happen if synchronous machine rotor fed from single phase ac supply 

1305


what is the difference between STAR and DELTA connection and application wise how it can be utilizedd

1739


what are pilot cells

1581


i have flexible wire. size of conductors is 0.190 mm & no.of conductors are 48. then size of wire comes 1.37 sqmm instead of 1.5 sqmm . the what is tolerance for this size.

1330


The power factor of the fixed load is 0.8, now the p.f is varying from 0.8 to 0.5.

1581


I have a relay contact rated at 220v dc which is supplied with a 24vdc from the panel,for it to trip the dampers(24vdc).What if the application of the relay changes so that it should work at its rated 220vdc then will it work at 24vdc supply given or any other consideration needs to be taken .....

1659


What is EHT tariff or Power factor Tariff ????

1913


What happen Grid EARTH plat got cut.

1748