Stator of 3-phase IM has 3 slots per pole per phase,
calculate number of stator pole pairs.
A 1 B 6
C 2 D 3
Answer Posted / shubham shukla
poles=2*(number of slots per pole per phase)=2*3=6
total no of slots=3 slots/pole/phase* 6 pole * 3 phase=54
| Is This Answer Correct ? | 4 Yes | 0 No |
Post New Answer View All Answers
please tell me when we start motor without load in star or delta connection whose current above condition,pl write formula
Pls mail me utility & Dg related question with answer
Whether should be the oil level in OCTC transfomer? It should be upto winding immersed completely or should be upto tap changer s/w? How it will affect the performance of the transformer. Rating may be 33KVA
What is the use of mc( moving coil) in dc voltmeter and dc ammter and what is the use of ( moving iron)in ac voltmeter nd ac ammeter
How to maintain ac plant?
How time response of the system is divided?
how to find motors H.P. whout any rating? (only give you a motor and multimeter)
How PSV sizing being done
what is the terminal voltage of dc series generator running at rated speed at no load?
1.dg on load alarm/stop alarm... 2.dg on load. piu alarm alarm kaise chek krte hai
is it possible to say motor horsepower number without seeing name plate(when name plate damaged)
Is there any guideline say about display of earthing value near to earth pit
What is value of earth resistance required for substation and equipment earthing and what are the reference guidelines
what is tri state logic gate
What are the basic properties of signal flow graph?