How to calculate voltage drop in copper and aluminium cable?
I have laid 240Sq.mm Aluminium cable for the length of 600 Mtrs in 1 Mtrs underground.
Normal load is 150A. Transformer is 630KVA, 6.KV/433V. But, I am getting only 395 Volts when load. How to calculate voltage drop and what is the permissible voltge drop for this circuit?
Answer Posted / viren89desai@yahoo.co.in
http://www.openelectrical.org/wiki/index.php?title=Cable_Sizing_Calculation
| Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
what is a pulse transformer? how rise time of pulse changes when ever the voltage changes?
what is the difference between vector scale and vector diagram?
what is the difference between rectifier and converter and commudator?
IF % IMPEDANCE OF A TRANSFORMER IS INCREASED FROM 5.8% TO 8% HOW MUCH THE EFFICIENCY OF THE TRANSFORMER WILL COME DOWN?
sir please send me iocl written test paper in my e-mail account. i'll be obliged to you........ thank u roshan
Difference between field rheostat and armature rheostat.
How to do stting of vl250 siemens MCCB
Can anyone please provide me details of MCCB/Contactor/SFU rating calculations for a motor feeder..for example 50 kw.. not from type-2 cordination chart. i want manual calculations..
how we can calculate chiller required ampear?
Working of microwave oven?
Why synchronous motor is used in power factor improvement,dc series in lift
rajha power sector details
send me any model test paper of clerical post of state bank of india.......
TRAFO 1. WHY BREATHER IS USED. 2. WHY OIL GOES DOWN IN CONSERVATOR TANK. 3. WHY WE ARE TAKING OIL SAMPLE TAKING FROM BOTTOM OF TRANSFORMER. 4. HOW TO CHECK IR VALUE OF TRANSFORMER. 5. WHY OLTC HAVING BUCHHOLZ TRIP ONLY; WHY NO ALARM. 6. OFF LOAD TAP CHANGER OPERATION PROCEDURE. 7. TR. SHUTDOWN / ISOLATION PROCEDURE. 8. WHEN THREE TRS. IN PARALLEL, ONE TR. IS NOT SHARING THE LOAD – WHAT IS REASON AND WHAT YOU WILL DO. 9. WHY TR. HAS OLTC IN HV SIDE. 10. WHAT IS % IMPEDANCE. 11. WHY TR. RATING IN MVA. 12. WHAT IS VECTOR GROUP IN TR. 13. CONDITION FOR PARALLEL OPERATION OF TRS. 14. WHAT IS TERTIARY WINDING. WHERE IT WILL BE. 15. IF TR. TRIP ON BUCHHOLZ OR TAP CHANGER RELAY, WHAT YOU WILL DO. 16. DIFFERENCE BETWEEN OIL TEMP. AND WINDING TEMP. PROTECTION 17. HOW WINDING TEMP. IS MEASURED IN CAST RESIN TR. 18. DIFFERENT TYPES OF FAULTS IN TR. Trafo - Page-1 of 2 19. WHAT HAPPENS WHEN TR. CHARGED FROM LV. 20. WHAT WILL YOU DO IF MEGGER READING SHOWS ZERO BETWEEN LV WINDING AND EARTH. 21. CAN WE INTERCHANGE BUCHHOLZ RELAY OF MAIN TANK AND OLTC TANK. 22. IF THE LINE BETWEEN BREATHER AND CONSERVATOR TANK 23. LOCKED, WHAT WILL HAPPEN DURING LOAD CYCLE. 24. WHAT IS THE FUNCTION OF OIL SEAL IN BREATHER. 25. WHAT ARE LOCATIONS FOR BUCHHOLZ RELAY FIXED IN POWER TR. 26. WHAT ARE CHECKS IN POWER TR. DURING MAINTENANCE. 27. WHAT IS IMPORTANT WHEN WE CHECK OLTC OPERATION DURING MAINTENANCE. Trafo - Page 2 of 2
What is method of calculating the fault current for a MDB, 50KW, 3PH, 415V, 50HZ?