Answer Posted / mugil
Assuming 24 vdc I/O cards.
On a transistor output card Sourceing is PNP or Active High. This means that you connect the output to the + side of the load device and connect the other side to 0vdc. If the output Card is Sinking it is NPN or active low meaning that you would tie the + side of the device to 24vdc and the common would connect to the output card.
On input cards if the input card is a sourceing card you would use NPN sensors. The cards common connection would be to a +24vdc source and the device (sensor) would give a path to 0vdc. If the input card was sinking you would use PNP sensors. The sensor would be connected to the + 24vdc source and the output from the device would connect to the PLC input card which would have a common connection to 0vdc.
Is This Answer Correct ? | 0 Yes | 1 No |
Post New Answer View All Answers
What care will you take in the installation of control valves,SCADA,DCS and FOC in Oil and Gas Project?
Somebody can explain me about >Critical Loops, calibrations, ESD critical Loop checks, Logic Diagram / Cause & Effect checks for ESD loops,
How to calibrate capillary type level transmitter
why we are using magnet for calibration of gas detector?
Linear amplifier.
what is the imbustion control loop
Draw a complete P&ID of a flow suction tank indicating all control & protection equipment. Indicate all its inlets and outlets. Explain the controls for this system
A DP transmitter is used to measure the level of an open tank. The drain line of the tank is connected to a control valve, and is configured as, if the level of the tank is 90% the valve should get open 10%. And if the tank level is 10%, the valve should get open 90%. Draw wiring diagram and explain how to configure DP transmitter and control valve using HART communicator. If the span error at output is 1%, what will be the %opening of the control valve at 60% level of the tank?
Name different parts of a pressure gauge.
what is KV and XV valve
please any body have most important data for study for saudi aramco test of instrument QC thanks email shahnaveedullah@gmail.com
What is heating effect?
Any body have know try work calculation ???
how to work static pressure sensore how to work dpt
How to fix back the valve actuator stem