What is the function of semicon in 33kv ht cable ?
Answer Posted / paramesha r l
Purpose of semiconducting layer is to maintain uniform distribution of Poynting vector i.e., P=ExH in insulator or otherwise power P=EXH densely concentrated at insulation point where two phase are comes in contact.
what Semiconducting layer does is equipotential over outer surface of insulating medium as it is like a free space.
Semiconducting layer needed to remove at termination i.e, 35 to 50 cm from lugs point.
If semiconducting layer not removed at termination leakage current flows between conductor to semiconducting which is hardly a distance of 5mm at eventually it fails.
| Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
what is feeder bay?
how to calculate vfd o/p voltage by frequency
What is the importance of earthing?
After taking shutdown of 11kv feeder, if you see 5kv by phasing stick in the cable side, is it possible to close earth switch in cable.
For an induction motor wat is the loading/unloading cycle duration or interms of L/UL ratio/ percentage?
what are the different kind of cables used for transmissions?
What will be the current if the resistance total in a series circuit doubles?
What are the classifications of heating element?
Two liquids hot and cold in two vessels are there and an metal bar acts as a conductor of heat between the two vessels. what happens then. what happens after 24 hrs?
In the formula : Knee point voltage = Burden X alf / class, Please inform what is alf? regards Shashidhar M.R.
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
how does directional relay work incase of ac ?
please explain to me how to calculate current,voltage,resistance with formula??
What is difference between insulating medium and fault current interruption medium in a switching device.
Advantages/Disadvantages of earthing of neutral bus on MSB instead of separate neutral earthing for transformer/DG sets feeding to MSB