hi... i'm about to learn siemens plc
i came across following question in my mind ... plr ans
1. hw motor operated by plc
2. hw drive operated by plc
explain dis by both ladder logic diagram and hardware config , connection
Answer Posted / dipesh shrivastava
All plc's work under four checks
Ai - Analog I/p
Ao- Analog o/p
Di - dig I/p
Do- Dig o/p
Commands like Motor on & Off are Do's
Commands like Drive operation, control valves operations means any type of partial operations between its low range and high range will be AO
Inputs are of 3 major types , (0-5) V DC, (0-10)v DC & (4-20) mA
All types of feedbacks like proximity ( PNP,Npn ) then feebbacks like actuator open/close, Motor on/off/trip, Feeder healthy/not healthy will be Digital inputs
| Is This Answer Correct ? | 1 Yes | 0 No |
Post New Answer View All Answers
What is the procedure of calibration of Load cell?
what is the working principal of pribe
why we should maintain neutral earth voltage below 1V while calibration? why cant it be 1.2V or 2V
A flange is used for instrument connection for a system with a design temperature of 316C (600F) and a design pressure of 1000 kPa (145 psi). What is the class rating of the flange to be used for this application? Explain your answer
How u measure the massflow in orifice flow measurement techniques
What is compensation for flow ? Why we use compensation ? What are the factors of different compensation ? We not use then what problems may happen ?
how to calibrate 0- 150 psi presure gauge by dead weght tester
How will you test a transistor with a multimeter?
Explain PID, ON/OFF, Controls
Can combine control system for Emergency control system (ESD)and Fire & Gas System ( F & G) is possble to built and offer to client? Can such system is as per Norms in India?
What is intrinsic safety mean.
What is sensitivity in vibration probes..?
1. For Steam drum level signal, why do we compensate with drum pressure signal? 2.For main steam Flow signal is comensated with main steam temperature signal and main steam pressure signal why?
How can we use feedback signal frm rtd for monitoring and in dcs for controlling ,then which type of rtd is sutaible 2 , 3,4wire and why ?
Whatis the reset ofset and control system in instrumentation