what is the safety of ACB & VCB and how can this work and
how can the service the ACB & VCB parts name with picture
Answer Posted / manny sood
Over voltage
Under voltage
Earth fault
Reverse power
, these are the safety of ACB,
High current
Earth fault
No moisture
, these are the safety of VCB
| Is This Answer Correct ? | 91 Yes | 7 No |
Post New Answer View All Answers
How earthing/grounding done in aeroplanes and ships.
What is step signal?
What shall be the secondary output voltage if the primary winding of a 220/6V, 50 Hz transformer is energized by an 110V, 60 Hz supply?
How many types of faults are there in 3 phase power system?
What is the lockout relay
Why do we need a separate control desk & PLC control panel in Boiler plant or coal handling plant? Can we provide cost effective Control desk cum PLC panel. Is there is an specific need for control desk.. kindly advice.
difference between main metering kiosk and check metering kiosk
How i can calculate current of cable according to ares?
Why is the air gap between the pole pieces and the armature kept very small?
what is the difference between changer, converter and transformer?
1. A bomber drops a bomb from an aircraft flying at 2000 km/hr. at an altitude of 7km. The speed at which the bomb will strike the earth would be
how we can decide that what value of ht line will come to any commercial building? (ans except According to the building load)
what are the advantages disadvantages of connecting high voltage block( 1:1 transformers) transformers between the turbo generators and busbars.
how flow current in 220 kv line to line
What is the emf equation of a transformer?