how to calculate the multiplying factor for energy meter
with CT ratio given
Answer Posted / manish borle
M.F.Of any energy meter is
M.F.=C.T. Ratio * p.T. Ratio * scale factor of the meter
Eg for ctr = 50/5 , ptr = 11000/110 , sf = 1/100
M.F. = 10
| Is This Answer Correct ? | 2 Yes | 2 No |
Post New Answer View All Answers
How you give clearance to a spare feeder.
what happen if generator of micro hydro running at only a small percentage of its capacity, as a comparison, if the diesel generator that runs on only a fraction of its capacity there will be a wet stacking
How a capacitor discharge weld power supply works? what is the use of a pulse transformer?
What do you mean by transformation ratio of instrument transformer?
Briefly describe means used by electricity suppliers to influence the flow of active and reactive power in power networks (one for each type)?
What is the rating of circuit breaker needed for 300 KVA load in 33 KV supply line in a transformer of 33 KV / 415 Volt ?
List of equipments required foe industrial repair lab.
features of hbc fuses
what is the formula of starting current of 3phase and 1 phase motor???
A power transformer 4MVA/11KV/0.415Kv has been out of use in 12years. what maintenance actions/test need to be carried out before energizing.
What happens if we run alternator on under frequency?
At what speed 1 HP motor can run an electric car of weighing 400 kg?
WHAT IS LOAD CELL
hi friends i m from electrical branch and seeking for tech. + apti. both papers of hpcl plz get it available as soon as possible
how many types control panel of a 132/33 kv substation